Subject: [OASIS Issue Tracker] Created: (EMIX-409) CIM Defintion Sources:CLONE -Power Quality Definitions CLONE -Omnibus issue for Acclara (DavidHaynes) comments


CIM Defintion Sources: CLONE -Power Quality Definitions CLONE -Omnibus issue for Acclara (David Haynes) comments
----------------------------------------------------------------------------------------------------------------

                 Key: EMIX-409
                 URL: http://tools.oasis-open.org/issues/browse/EMIX-409
             Project: OASIS Energy Market Information Exchange (eMIX) TC
          Issue Type: Improvement
    Affects Versions: csprd02 Public Review Draft
         Environment: David Haynes
            Reporter: Toby Considine
            Assignee: Aaron Snyder 


820     technical       "Flicker" is not defined. By what standard is flicker to be quantified? Westinghouse? IEEE? What about the severity of the flicker? Not all flicker events are the same yet you treat them as if they were. I suggest you look at the IEEE 519 std. What you have modeled here isn't useful.

820     technical       "Voltage dips" are not defined. What constitutes a voltage dip? What is the threshold and duration? Suggest you look at IEEE std. 1564. 

820     technical       "short interruptions" and "long interruptions" are not defined. These are non-standard terms. You must either define what you mean or cite another document that will do that for you. I suggest you refer to IEEE 1366 and use the standard terminology, metrics, and definitions. (i.e. "momentary interruption," "momentary interruption event," "sustained interruption," etc.) What you have here is completely unusable in the industry. We all subscribe to and use the IEEE 1366 indices.

820     technical       "temp overvoltage" is not defined. This is a non-standard term. Suggest you use the term "voltage surge". You should look at IEEE stds. 1564 or 1159 or IEC 61000-X.

820     technical       "supply voltage imbalance" is not defined. What constitutes an imbalance? This is usually defined by a percentage (or PU) level. Where do you define the severity and duration of an imbalance event? These have to be defined before they are counted!

820     technical       "harmonic voltage" there are an unlimited number of harmonics possible. Which one(s) are you measuring here? Suggest you look at IEC 61968-9 Ed. 2. Annex C and IEEE 519.

820     technical       Why is the word "signaling" in the definition for mains voltage? Our company makes a product that communicates on the powerline. Few others do. I propose that you change this to describe the secondary voltage delivered to the service point (if that is what you are trying to define here.)

-- 